    Post

    When using PVC between the meter base and the disconnect, is a bond required to be added. If metal conduit is used what prevents parallel current flow?

  2. #2
    Inactive Member Cosimo Diano's Avatar
    Join Date
    March 27th, 2004
    Posts
    36
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    No bond is required when using a meterbase with a non-insulated neutral block and we need not worry about parallel paths when using steel conduit. This is why: Rule 10-204 (1) (d) Alternating-current circuits which are to be grounded shall have no connection between the grounded circuit conductor on the "load" side of the service disconnecting means and the grounding electrode. App. B 10-204(1) The supply side of the disconnecting means is deemed to include all of the interior of the service box.

  3. #3
    Inactive Member Cosimo Diano's Avatar
    Join Date
    March 27th, 2004
    Posts
    36
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    My post above applies when the meterbase is ahead of the service box.