When using PVC between the meter base and the disconnect, is a bond required to be added. If metal conduit is used what prevents parallel current flow?
-
January 2nd, 2005, 11:02 PM
#2
Inactive Member
No bond is required when using a meterbase with a non-insulated neutral block and we need not worry about parallel paths when using steel conduit. This is why: Rule 10-204 (1) (d) Alternating-current circuits which are to be grounded shall have no connection between the grounded circuit conductor on the "load" side of the service disconnecting means and the grounding electrode. App. B 10-204(1) The supply side of the disconnecting means is deemed to include all of the interior of the service box.
-
January 2nd, 2005, 11:06 PM
#3
Inactive Member
My post above applies when the meterbase is ahead of the service box.